m (→txButton()) |
(111 intermediate revisions by 6 users not shown) | |||
Line 1: | Line 1: | ||
=RaceCapture/Pro Scripting Guide= | |||
A large collection of example scripts can be found in our '''[[RaceCapturePro Lua Scripting Examples|Lua Scripting Examples]]''' | |||
'''[[RaceCapturePro Lua Scripting Examples|Lua Scripting Examples]] | The [https://www.lua.org/manual/5.1/ Lua Reference Manual] can be found on [https://www.lua.org/ Lua.org] | ||
==Lua Script Basics== | |||
===Conventions=== | |||
* All inputs and outputs are numbered starting at 0 (getGpio(0), setChannel(0), etc) | |||
* All channel values must be numbers | |||
* All virtual channel names must have no spaces (to be fixed in future revisions) | |||
====Writing your script==== | |||
=====onTick() function===== | |||
Your Lua script is centered around the onTick() function. RaceCapture/Pro will periodically call this function, and here you can define your custom tasks and logic. | |||
Example: this script will periodically write a message to the log: | |||
<pre> | |||
function onTick() | |||
println("hello from RaceCapture/Pro") | |||
end | |||
</pre> | |||
=====Viewing the output log===== | |||
You can observe the loading of new script and monitor and debug the behavior of your script by using the print() / println() functions. In order to see the log output, enable the "Poll Log" checkbox in the scripting window: | |||
[[image:Hello_RaceCapturePro_script.png|800px]] | |||
=====Controlling the onTick() rate===== | |||
You can control how fast your script is executed using the setTickRate() function. The tick Rate is specified in Hz, and the default rate is 1Hz, maximum of 1000Hz. | |||
* '''Note:''' actual tick rates may be slower based on the amount of processing time in your onTick() handler. | |||
<pre> | |||
count = 0 | |||
setTickRate(10) | |||
count = count + 1 | |||
println("Tick: " ..count) | |||
end | |||
</pre> | |||
[[image:RaceCapture_tick_count.png|800px]] | |||
=====Reading and controlling inputs and outputs===== | |||
The Lua scripting enables endless combinations of custom behaviors by reading sensor values, controlling output lines, broadcasting CAN messages and writing data to the Auxiliary serial port. | |||
Example: Reading a sensor value and activating an output based on a threshold. | |||
Given: | |||
* A calibrated temperature sensor is connected to the first analog input (0); | |||
* The first GPIO is configured for output mode | |||
This script will activate the output upon crossing the temperature threshold of 212. | |||
<pre> | |||
temperature = getAnalog(0) | |||
if temperature > 212 then | |||
setGpio(0, 1) | |||
else | |||
setGpio(0, 0) | |||
end | |||
end | |||
</pre> | |||
=====Combining multiple functions===== | |||
When combining multiple functions into one script, it's recommended to break them into multiple functions and reference them from the main onTick() function. | |||
Example: | |||
<pre> | |||
function checkTemps() | |||
[ temperature checking logic goes here ] | |||
end | |||
function checkAutoLogging() | |||
[ automatic logging logic goes here ] | |||
end | |||
checkTemps() | |||
end | |||
</pre> | |||
==Troubleshooting== | |||
===Debugging your script=== | |||
If you're not sure why your script is misbehaving, you can use the println() function to output messages in the log and observe how your script is behaving. | |||
Example: | |||
<pre> | |||
println("current temp: " ..temperature) | |||
println("over temp!") | |||
setGpio(0, 1) | |||
else | |||
println("under temp") | |||
setGpio(0, 0) | |||
end | |||
end | |||
</pre> | |||
===Out of memory issues=== | |||
If you are seeing out of memory issues, try the following: | |||
====Mark variables in your script as local==== | |||
Lua makes variables global by default, which is typically opposite of other programming languages. Since global variables consume more memory, try making variables declared in your function local: | |||
<pre> | |||
function addSomeNumbers() | |||
local var1 = 3 | |||
local var2 = 5 | |||
return var1 + var2 | |||
end | |||
</pre> | |||
====Reduce extra comments, large string variable declaration and other bloat==== | |||
* Remove comments, shorten the size of any text strings you define - these all consume memory. | |||
====Simplify your script==== | |||
* Reduce the number of variables at the top, and inline their usage in the script. This will help reduce the amount of global memory uses. | |||
* Evaluate the functions you define. Sometimes it makes sense to combine your code into fewer functions, if it turns out you only call that function once. Other times, you may need to break out a function to save space, if you need that function repeatedly. | |||
====Call the garbage collector periodically==== | |||
If your script is very close the limits of memory, regularly calling the garbage collector may help. Calling collectgarbage() in the onTick() is recommended:<pre> | |||
collectgarbage() | |||
-- other code -- | |||
end | |||
</pre> | |||
====Try a Lua minimizer==== | |||
Minimizing/Minifying your script will compact your script, at the expense of making it harder to read. You can try an [https://mothereff.in/lua-minifier online minifier] to see if that makes a difference. | |||
* Since it makes your script harder to maintain, we recommend this as a last resort. | |||
=Lua Reference= | |||
RaceCapture/Pro uses the standard, lightweight Lua scripting language used as an extension / customization language for many software applications and especially gaming. | |||
* See [https://www.lua.org/ lua.org] for additional information on how to use the Lua language | |||
=More examples= | |||
You can see more examples in our [[RaceCapturePro Lua Scripting Examples|Lua Scripting Examples]] section. | |||
=API Reference= | |||
==General Input / Output (GPIO) Functions== | ==General Input / Output (GPIO) Functions== | ||
Line 13: | Line 170: | ||
Line 21: | Line 179: | ||
*params | *params | ||
** channel: integer 0 - 2 | ** channel: integer 0 - 2 | ||
** state: (int / ''(since 2.10.0)'' bool) 1 / true = output active; 0 / false = output inactive | |||
*returns: | *returns: | ||
** none | ** none | ||
Line 35: | Line 194: | ||
*returns | *returns | ||
'''PWM / Analog outputs only apply to RaceCapture/Pro MK1 and MK2'' | |||
===setPwmDutyCycle( channel, dutyCyclePct )=== | ===setPwmDutyCycle( channel, dutyCyclePct )=== | ||
Line 44: | Line 204: | ||
** channel: PWM / Analog output channel 0 - 3 | ** channel: PWM / Analog output channel 0 - 3 | ||
** dutyCyclePct: Percentage value of the duty cycle as a counting number 0 - 100 | |||
=== | ===setPwmClockFreq( frequency )=== | ||
Sets the | Sets the clock frequency of the PWM outputs | ||
** | ** frequency: the frequency of the PWM clock, in Hz. Supported range is 320-40000 Hz | ||
* | * returns | ||
* | ** none | ||
* none | |||
===setAnalogOut( channel, voltage )=== | ===setAnalogOut( channel, voltage )=== | ||
Line 71: | Line 231: | ||
** channel: Timer channel 0 | ** channel: Timer channel. Zero based, so first channel is 0, 2nd channel is 1, and so on. | ||
** returns: RPM value | ** returns: RPM value | ||
Line 78: | Line 238: | ||
** channel: Timer channel 0 - 3 | ** channel: Timer channel 0 - 3. Zero based, so first channel is 0, 2nd channel is 1, and so on. | ||
** returns: millisecond value | ** returns: millisecond value | ||
Line 85: | Line 245: | ||
** returns: Frequency in Hz | ** returns: Frequency in Hz | ||
Line 92: | Line 252: | ||
** returns: Raw timer value between 0 - 65535 | ** returns: Raw timer value between 0 - 65535 | ||
Line 103: | Line 263: | ||
===getAnalog(channel)=== | ===getAnalog(channel)=== | ||
Reads the scaled analog value for the specified analog input channel. | Reads the scaled analog value for the specified analog input channel. | ||
** channel: Analog input channel 0 | ** channel: Analog input channel. Zero based, so first channel is 0, 2nd channel is 1, and so on. | ||
*** Note: the last Analog input is connected to battery voltage: | |||
**** Channel 7 on RaceCapture/Pro MK1 and MK2 | |||
****Channel 8 on RaceCapture/Pro MK3 and RaceCapture Apex | |||
==Accelerometer / Yaw Sensor Functions== | ==Accelerometer / Yaw Sensor Functions== | ||
=== | ===getImu(channel)=== | ||
Reads the specified | Reads the specified IMU channel | ||
* params | * params | ||
** channel (0 | ** channel (0 = X, 1 = Y, 2=Z, 3= Yaw, 4= Pitch, 5 = Roll) | ||
* returns | * returns | ||
** The value scaled to G force, or degrees/sec depending on the channel selected | ** The value scaled to G force, or degrees/sec depending on the channel selected | ||
=== | ===getImuRaw(channel)=== | ||
Reads the raw | Reads the raw value of the specified accelerometer or yaw channel | ||
** The raw accelerometer value | ** The raw accelerometer value | ||
Line 146: | Line 311: | ||
** (none) | ** (none) | ||
** The current GPS quality indicator | ** The current GPS quality indicator | ||
** 0: No fix; 1: Fixed; 2: SPS Fix; 3: Differential Fix | |||
===getGpsSats()=== | |||
* params | |||
** (none) | |||
* returns | |||
** The number of GPS satellites currently used in the fix | |||
===getGpsTime()=== | ===getGpsTime()=== | ||
Line 161: | Line 333: | ||
** The distance, in Miles | ** The distance, in Miles | ||
===getGpsAltitude()=== | |||
Provides the current GPS calculated altitude from sea level in feet. The method will return 0 if there is no GPS lock. | |||
* Added: v2.9.0 | |||
* Parameters: ''None'' | |||
* Returns: <altitude> | |||
===getGpsSec()=== | |||
* params | |||
** (none) | |||
* returns | |||
** number of seconds since midnight, as measured by the attached GPS module | |||
==Lap Statistics== | |||
Line 176: | Line 363: | ||
** The last measured lap time in decimal minutes / seconds | ** The last measured lap time in decimal minutes / seconds | ||
=== | ===getPredTime()=== | ||
Provides the | ''as of 2.12.0 firmware'' | ||
Provides the current Predicted Lap time time as determined by the start/finish line configuration and measured by the attached GPS module. A training lap is required before the predicted time is valid. | |||
** | ** The current predicted time in decimal minutes / seconds | ||
Line 188: | Line 377: | ||
=== | ===resetLapStats()=== | ||
''since 2.16.0'' | |||
** | ** (none) | ||
** | ** (none) | ||
=== | ==Time Functions== | ||
===getTickCount()=== | |||
None | |||
Line 213: | Line 404: | ||
** channel: The CAN channel. 0 for the first channel, 1 for the 2nd, if supported on the hardware | ** channel: The CAN channel. 0 for the first channel, 1 for the 2nd, if supported on the hardware | ||
** baud rate: Supported baud rates: 100000, 125000, 250000, 500000, 1000000 | ** baud rate: Supported baud rates: 100000, 125000, 250000, 500000, 1000000 | ||
** termination: 1 to enable termination, 0 to disable. Defaults to 1 (enabled) ''Only available on RaceCapture/Pro MK3 and RaceCapture/Apex. On other platforms this setting has no effect''. | |||
** 1 if successful, 0 if initialization fails | ** 1 if successful, 0 if initialization fails, nil if parameters are incorrect | ||
===txCAN(channel, id, isExtended, data )=== | ===txCAN(channel, id, isExtended, data, [timeout] )=== | ||
Transmit a CAN message. | Transmit a CAN message. | ||
Line 223: | Line 415: | ||
** identifier: The Identifier value of the message, either in standard (11 bit) or extended (29 bit) format. | ** identifier: The Identifier value of the message, either in standard (11 bit) or extended (29 bit) format. | ||
** isExtended: 0 for Standard (11 bit) Identifier or 1 for Extended (29 bit) Identifier. | ** isExtended: 0 for Standard (11 bit) Identifier or 1 for Extended (29 bit) Identifier. | ||
** | ** data: CAN message payload; array up to 8 elements long. | ||
** timeout: (optional) specify a timeout for sending this message. if the transmit queue is full, will block for the specified milliseconds. Defaults to 100ms | |||
* returns | |||
** 1 if successful, 0 if failed, nil if parameters are incorrect | |||
Example: | Example: | ||
channel = 0 | |||
id = 1234 | id = 1234 | ||
ext = 0 | ext = 0 | ||
data = {11,22,33} | data = {11,22,33} | ||
res = txCAN(id, ext, data) | res = txCAN(channel, id, ext, data) | ||
===rxCAN(channel, timeout )=== | ===rxCAN(channel, [timeout] )=== | ||
Receive a CAN message, if available. | Receive a CAN message, if available. | ||
** timeout (optional). read timeout in milliseconds | ** timeout (optional). read timeout in milliseconds. defaults to 100ms. For non-blocking functionality specify a timeout of 0. | ||
Line 242: | Line 439: | ||
** Data: CAN message payload; array up to 8 elements long. | ** Data: CAN message payload; array up to 8 elements long. | ||
If no CAN message was received, the function returns | If no CAN message was received, the function returns nil | ||
id, ext, data = rxCAN(100) --100ms timeout | id, ext, data = rxCAN(0, 100) --100ms timeout | ||
if id ~= nil then | if id ~= nil then | ||
println("CAN rx: " ..id .." " ..data[1]) --print ID and first element of received message | println("CAN rx: " ..id .." " ..data[1]) --print ID and first element of received message | ||
Line 252: | Line 449: | ||
===setCANfilter(channel, filterId, extended, filter, mask )=== | ===setCANfilter(channel, filterId, extended, filter, mask )=== | ||
Sets the specified CAN filter ID, to ignore messages | Sets the specified CAN filter and mask ID, to ignore CAN messages that match a particular ID pattern. | ||
Line 260: | Line 457: | ||
** mask: the mask for the CAN filter | ** mask: the mask for the CAN filter | ||
* 1 for success, 0 for fail | ** 1 for success, 0 for fail, nil if parameters are incorrect | ||
==OBDII functions== | |||
Line 269: | Line 467: | ||
* params | |||
* returns | |||
** none | |||
Line 279: | Line 487: | ||
The onTick() function is the main loop where scripting activity takes place. By default it is called by RaceCapture/Pro every 1 second (1Hz). The rate can be adjusted using the setTickRate() function. | The onTick() function is the main loop where scripting activity takes place. By default it is called by RaceCapture/Pro every 1 second (1Hz). The rate can be adjusted using the setTickRate() function. | ||
* '''Note''' - you should only define one onTick() function in your code. If multiple onTick() functions are defined, only the last defined onTick() function will be used. | |||
Line 289: | Line 499: | ||
Sets the rate at which the onTick() function is called | Sets the rate at which the onTick() function is called | ||
** rate: The rate the onTick() function is called, in Hz. Max tick rate is | ** rate: The rate the onTick() function is called, in Hz. Max tick rate is 1000Hz. | ||
==SD Logging control== | |||
The following functions control logging operations to the internal SD card. | |||
* '''Note:''' Only SD card logging is controlled; External devices or apps connected to the telemetry stream are not affected by these commands. | |||
===isLogging()=== | |||
Indicates if an SD card logging session is in progress | |||
* params | |||
** (none) | |||
* returns | |||
** 0 if not logging, non zero otherwise. | |||
===startLogging()=== | ===startLogging()=== | ||
Begins a logging session | Begins a logging session to the SD card. If currently logging, this function has no effect. | ||
* '''Note:''' If an error occurs during writing, the error indicator on the front panel, if provided, will illuminate. | |||
Line 301: | Line 523: | ||
===stopLogging()=== | ===stopLogging()=== | ||
Stops the current logging session. If not logging, this function has no effect. | Stops the current SD card logging session. If not logging, this function has no effect. | ||
Line 311: | Line 533: | ||
** led (1-3) | ** led (1-3) | ||
** state : 1 = on, 0 = off | ** state: (int / ''[as of 2.10.0]'' bool) 1 / true = on, 0 / false = off | ||
=== | ===setBgStream( on/off )=== | ||
Sets the state of background streaming | |||
* params | |||
** Boolean: true for on, false for off. | |||
* returns | |||
** (none) | |||
===getBgStream()=== | |||
Gets the state of background streaming | |||
* params | |||
** (none) | |||
* returns | |||
** Boolean: True for on, false for off. | |||
==Serial Port Communications== | |||
These function calls allow reading / writing line oriented data from the built in serial ports. | |||
===Port mappings=== | |||
* 0 = USB port<br/> | |||
* 1 = GPS port<br/> | |||
* 2 = Internal telemetry port (MK2/3/Apex only)<br/> | |||
* 3 = Bluetooth port<br/> | |||
* 4 = Auxiliary / WiFi port<br/> (RaceCapture/Pro MK2) | |||
* 5 = WiFi port | |||
* 6 = External Auxiliary port (RaceCapture/Pro MK3 and RaceCapture/Apex only) | |||
* '''Note''': We only recommend using the designated auxiliary port for your hardware model The other ports have been included for reference; using them may interfere with normal operations of the unit. | |||
===initSer( port, baud, bits, parity, stopBits)=== | |||
Initializes the specified serial port | |||
* params | |||
** port: The port to initialize. (defaults to Auxiliary port) | |||
** baud: The baud rate to set (defaults to 115200) | |||
** bits: Number of bit in the message (8 or 7) (defaults to 8) | |||
** parity: (1 = Even Parity, 2 = Odd Parity, 0 = No Parity) (defaults to No Parity) | |||
** stopBits: number of stop bits (1 or 2) (defaults to 1) | |||
* returns | |||
** true if initialization succeeds | |||
===readCSer( port, [timeout])=== | |||
''Available since firmware 2.8.4''<br> | |||
Read a character from the specified serial port | |||
** port: | ** port: The port to read. (required) | ||
** | ** timeout - the read timeout, in ms. | ||
* returns | |||
** the character read, or nil if the timeout was reached | |||
=== | ===readSer( port, [timeout])=== | ||
Read a line of data from the specified serial port. This command blocks until a newline ('\n') character is received on the port, or a timeout occurs. | |||
** port: Serial port 0 - | ** port: Serial port 0 - 4 | ||
** timeout - the read timeout, in ms. | |||
** returns: a line of serial data, or nil if the timeout was reached | |||
===writeCSer( port, data )=== | |||
Writes the specified character to the serial port. The call will block until the character is written. | |||
* params: | |||
** port - the serial port to write | |||
** char - the character to write. | |||
* returns: | |||
(no return values) | |||
===writeSer( port, data )=== | |||
Writes a line of data to the specified serial port, appending a newline at the end. The call will block until all characters are written. | |||
* params | |||
** port: Serial port 0 - 4 | |||
** data: the data in string format | ** data: the data in string format | ||
* returns: | |||
==Logger Configuration Functions== | ==Logger Configuration Functions== | ||
Line 359: | Line 648: | ||
==Virtual Channels== | ==Virtual Channels== | ||
===addChannel( name, sampleRate )=== | ===addChannel( name, sampleRate, [precision], [min], [max], [units] )=== | ||
Adds a virtual channel. This virtual channel remains in memory during runtime; it is not persisted in the configuration. Up to | Adds a virtual channel. This virtual channel remains in memory during runtime; it is not persisted in the configuration. Up to 100 virtual channels can be created. | ||
** name: The name of the channel | ** name: The name of the channel, up to 10 characters long. We recommend using an existing System channel name as defined by the app when possible. | ||
** sampleRate: A supported sample rate (1,10,25,50,100,200Hz) | ** sampleRate: A supported sample rate (1,10,25,50,100,200Hz) | ||
** precision: (optional) the numerical precision (number of decimal places) used when logging to SD and telemetry. Defaults to 2 | |||
** min: (optional) The min expected value for this channel. Defaults to 0 | |||
** max: (optional) The max expected value for this channel. Defaults to 1000 | |||
** units: (optional) The units label for this channel. Defaults to empty string / none | |||
** the | ** the id of the new virtual channel, or NIL if the virtual channel could not be created. Use this id for setting the channel value (see setChannel() ) | ||
===getChannel( Channel ID or name )=== | |||
* First available in v2.9.0 ; retrieving by channel name available in v2.13.0 | |||
* Parameters | |||
** Channel ID or name : if a number, matches on the channel ID as provided by the '''addChannel''' function. If string, matches on any current channel in the system. | |||
* Returns | |||
** (number) The current value of the channel if available, or '''nil''' if the value is not available. You should always check if the value is present before using it for other purposes, especially if the script's tick rate is high relative to the channel's sample rate. | |||
* Examples: | |||
--returns the virtual channel assigned to ID 1. Current value of channel is stored in val | |||
val = getChannel(1) | |||
--get the channel by name | |||
rpm = getChannel("RPM") | |||
if rpm ~= nil then | |||
println("rpm channel: " ..rpm) | |||
end | |||
===setChannel( channelId, value )=== | ===setChannel( channelId, value )=== | ||
Line 372: | Line 684: | ||
Updates the value of a previously created virtual channel. | Updates the value of a previously created virtual channel. | ||
** | ** channelId: the ID of the channel provided by addChannel() | ||
** | ** value: the new value to set for the virtual channel | ||
id = addChannel("EGT", 1) | id = addChannel("EGT", 1) | ||
Line 384: | Line 696: | ||
setChannel(id, temp) --sets the virtual channel value | setChannel(id, temp) --sets the virtual channel value | ||
end | end | ||
==Time Info== | |||
These methods get you information about dates and time. This is useful in controlling script behavior or just knowing what time it is. | |||
===getUptime()=== | |||
Returns the number of miliseconds since the device last started. This is always available and is the most consistent way to time things in LUA script on RaceCapture. | |||
* Returns | |||
** Number of milliseconds since CPU boot. | |||
===getDateTime()=== | |||
Returns date and time info to the best of the systems ability, in UTC. Only available after GPS lock has been established. Will return epoch time (Jan 1, 1970 00:00:000) if time is not available. | |||
* Returns: A list of date and time information in the following order: | |||
** Year | |||
** Month | |||
** Day | |||
** Hour | |||
** Minute | |||
** Second | |||
** Millisecond | |||
==Dashboard Control== | |||
===txButton()=== | |||
* params | |||
* returns | |||
** (nothing) | |||
==ShiftX2/3 control== | |||
===sxSetConfig()=== | |||
<pre> | |||
sxSetConfig() | |||
</pre> | |||
* params | |||
* returns | |||
===sxCfgLinearGraph()=== | |||
* params | |||
* returns | |||
===sxSetLinearThresh()=== | |||
* params | |||
* returns | |||
===sxUpdateLinearGraph()=== | |||
* params | |||
* returns | |||
** (none) | |||
===sxSetAlert()=== | |||
* params | |||
* returns | |||
===sxSetAlertThresh()=== | |||
* params | |||
* returns | |||
===sxUpdateAlert()=== | |||
* params | |||
* returns | |||
===sxSetDisplay()=== | |||
* params | |||
* returns | |||
===sxSetLed()=== | |||
* params | |||
* returns | |||
===sxRxButton()=== | |||
* params | |||
** (none) | |||
* returns | |||
** button_id (ID of button. left button = 0, right button = 1) | |||
<pre> | |||
</pre> | |||
==Helper Functions== | |||
===calcGear()=== | |||
* params | |||
* returns | |||
<pre> | |||
</pre> | |||
* params | |||
** Speed Channel name | |||
** RPM Channel name | |||
* returns | |||
<pre> | |||
</pre> |
Revision as of 21:22, 1 January 2024
Lua Script Basics
Writing your script
onTick() function
function onTick() println("hello from RaceCapture/Pro") end
count = 0 setTickRate(10) function onTick() count = count + 1 println("Tick: " ..count) end
Given:
function onTick() temperature = getAnalog(0) if temperature > 212 then setGpio(0, 1) else setGpio(0, 0) end end
Example:
Example:
function onTick() temperature = getAnalog(0) println("current temp: " ..temperature) if temperature > 212 then println("over temp!") setGpio(0, 1) else println("under temp") setGpio(0, 0) end end
Try a Lua minimizer
Lua Reference
More examples
API Reference
getGpio( channel )
- params
- channel: integer 0 - 2
- returns:
- params
- returns:
- none
getButton()
- params
- none
- returns
- params
- returns
- none
- params
- returns
- none
- params
- returns
- none
Timer / RPM Sensor Functions
getTimerRpm(channel)
- params
- returns: RPM value
getTimerPeriodMs(channel)
- params
- returns: millisecond value
getTimerFreq(channel)
- params
- returns: Frequency in Hz
getTimerRaw(channel)
- params
Analog Sensor Functions
getAnalog(channel)
- params
getImu(channel)
- params
- returns
getImuRaw(channel)
- params
- returns
- The raw accelerometer value
GPS Sensor Functions
getGpsPos()
- params
- none
- returns
getGpsSpeed()
- params
- (none)
- returns
- The current speed in MPH
getGpsQuality()
- params
- (none)
- returns
getGpsSats()
- params
- (none)
- returns
getGpsTime()
- params
- (none)
- returns
- The current GPS time value
getGpsDist()
- params
- (none)
- returns
- The distance, in Miles
getGpsAltitude()
- Added: v2.9.0
- Parameters: None
- Returns: <altitude>
getGpsSec()
- params
- (none)
- returns
Lap Statistics
getLapCount()
- params
- (none)
- returns
getLapTime()
- params
- (none)
- returns
getPredTime()
- params
- (none)
- returns
getAtStartFinish()
- params
- (none)
- returns
resetLapStats()
since 2.16.0
- params
- (none)
- returns
- (none)
Time Functions
getTickCount()
- params
None
- returns
CAN Bus functions
initCAN(channel, baud )
- params
- returns
- params
- returns
Example:
- params
- returns
Example:
- params
- returns
OBDII functions
readOBD2( PID )
- params
- returns
- params
- returns
- none
onTick()
- params:
- (none)
- returns:
- (none)
Example:
setTickRate(rate)
- params
- returns
- (none)
SD Logging control
isLogging()
- params
- (none)
- returns
startLogging()
- params
- (none)
- returns
- (none)
stopLogging()
- params
- (none)
- returns
- (none)
setLed( led, state )
- params
- led (1-3)
- returns
- (none)
- params
- returns
- (none)
getBgStream()
- params
- (none)
- returns
Port mappings
- 0 = USB port
- 1 = GPS port
- 3 = Bluetooth port
- 4 = Auxiliary / WiFi port
- params
- returns
- params
- returns
- params
- port: Serial port 0 - 4
- params:
- returns:
(no return values)
- params
- returns:
(no return values)
flashLoggerCfg()
- params
- (none)
- returns
- (none)
setPwmClockFreq( freq )
- params
- returns
- (none)
getPwmClockFreq()
- params
- (none)
- returns
calibrateImuZero()
- params
- (none)
- returns
- (none)
Virtual Channels
- params
- returns
- Parameters
- Returns
- Examples:
--get the channel by name rpm = getChannel("RPM") if rpm ~= nil then println("rpm channel: " ..rpm) end
- params
Example:
id = addChannel("EGT", 1) function onTick() temp = getAnalog(0) --read analog channel 0 temp = temp * 1000 setChannel(id, temp) --sets the virtual channel value end
Time Info
getUptime()
- Returns
getDateTime()
- Year
- Month
- Day
- Hour
- Minute
- Second
- Millisecond
Dashboard Control
txButton()
- params
- returns
- (nothing)
ShiftX2/3 control
sxSetConfig()
sxSetConfig()
- params
- returns
sxCfgLinearGraph()
- params
- returns
sxSetLinearThresh()
- params
- Red: Red LED value (0-255)
- Flash: 0-10Hz (0 = sold on)
- returns
- params
- returns
- (none)
sxSetAlert()
- params
- returns
sxSetAlertThresh()
- params
- returns
sxUpdateAlert()
- params
- returns
sxSetDisplay()
- params
- Digit index (must be 0)
- returns
sxSetLed()
- params
- returns
sxRxButton()
- params
- (none)
- returns
- button_id (ID of button. left button = 0, right button = 1)
local id, state = sxRxButton() if id ~= nil then println('button ' ..id ..' state ' ..state) end
Helper Functions
calcGear()
- params
- returns
local gear = calcGear(62.7, 3.45, 4.23, 2.52, 1.66, 1.22, 1.0, 0.8) if gear ~= nil then println('gear: ' ..gear) end
- params
- Speed Channel name
- RPM Channel name
- returns
local gear = calcGear('Speed', 'RPM', 62.7, 3.45, 4.23, 2.52, 1.66, 1.22, 1.0, 0.8) if gear ~= nil then println('gear: ' ..gear) end