RaceCapturePro Sensors
Revision as of 03:30, 5 April 2019 by Brentp (talk | contribs) (→Sensors)
GM-Style
  • Wells SU109
  • SMP TX3
  • Pigtail: Pico 5615pt
Use the available Preset
  • Wells SU107
  • SMP AX1
  • Pigtail: Pico 5616pt
AEM
  • Delphi 12160855 equivalent
  • AEM-30-2012 Equivalent
  • Extended temperature range - suitable for coolant and oil
  • 1/8" NPT
0.40 302.00
0.87 239.00
1.88 176.0
3.2 122.0
4.72 32.0
Infrared Sensors
Mfg / Part # Image Notes
Thermocouple Sensors
Pressure Sensors
Fluid Pressure
  • Technical Specifications
Volts Scaled Value (PSI)
0.5 0.0
4.5 150.0
4.5 150.0
4.5 150.0
4.5 150.0
  • Sensor: 12223861 (GM)
  • vacuum port
3 bar MAP sensor
Volts Manifold Pressure (KPa)
0 3.6
1.25 80.0
2.5 159
3.75 237
5.0 315.0
Freescale MXP4250AP
2.5 bar MAP sensor
Tire Pressure
Schrader
  • OEM TMPS System
Pulse/Speed/RPM Sensors
Autosport Labs CoilX The CoilX sensor module is designed to safely interface the noisy, high voltage RPM signal at the ignition coil pack primary into a clean signal that RaceCapture/Pro can process.
Wheel Speed / Gear speed
Mfg / Part # Image Notes Pulse Channel Configuration
Hamlin 55505
  • Simple 3 wire hookup - No external pullup resistor required
  • -40 to 125c operation
Cherry GS100701
Distance Sensors
Ride Height
Sharp GP2D12
Steps to calibrate:
  7. Create Calibration Table:
  • Place the droop voltage / distance combination into the 1st column of the calibration table. Make the distance negative
  • Place the 'at rest' voltage into the 2nd column of the calibration table. Make the distance zero
  • BMW 37140141444
  • Pigtail: 61138383300
  • 5v power supply
  • Approximately 0-5v output
Texense RHS
KA Sensors RHL3
Angle / Rotation Sensors
Throttle Position (TPS)
Ford / SMP TH45
Screw mounted, keyed input for throttle shaft
Air / Fuel Ratio Sensors
Texense LSU 4.9 Sensor
Built-in wiring Screws into O2 sensor port
LSU 4.9 sensor
calibration
Volts Scaled (AFR)
0.004 8.4
1.36 11.3
2.3 14.0
2.879 18.4
3.395 26.7
Wiring Analog Sensors
  • Input Impedance: over 1 meg ohm
Calibrating an Analog Sensor
Refer to your sensor's data sheet for the sensor's calibration curve.
Linear Sensors
A linear sensor may specify two voltages/value pairs representing a low and high range for the sensor. A straight line is drawn between the points on the sensor.
Example: 150 PSI pressure sensor
  • 0.5 v = 0 PSI
  • 4.5 v = 150 PSI
Curved Sensors
These are often seen with thermistor based temperature sensors, where the response is not a straight line, but a curve. Multiple points can be used to sufficiently approximate the curve.
  • Note: RaceCapture will linearly interpolate the scaled values between the sensor points, so value transitions will be smooth.
Example: Extended Range temperature sensor with 5v reference and 2.2K pullup resistor
  • 0.4 v = 302 F
  • 0.87 v = 239 F
  • 1.88 v = 176 F
  • 3.2 v = 122 F
  • 4.72 v = 32 F
  • Note: If you have more than 5 points for the curve, spread the selection of points evenly between your low and high range.
Types of Sensors
Temperature Sensor
Pullup resistor
Sensor Ground
Active Sensors
  • Power
  • Ground
  • Signal Output
Wiring the Speed Sensor
  • Power: Connect the sensor's power to the 5v Vref on RaceCapture/Pro
  • Ground: Connect the sensor's ground connection to the ground shared by RaceCapture/Pro
  • Sensor Output: Connect the Sensor Output to one of RaceCapture/Pro's timer input channels
Optional pull up resistor
  • Throttle Position Sensors
  • Linear sensors
  • String Potentiometers
  • Fuel Level Sensors
Standard Variable Resistor (Potentiometer)
These are typically found in Throttle Position Sensors (TPS), string potentiometers, and linear sensors.
Fuel Level Sensors
Also a variable resistor, these provide a variable resistance based on the level of the float.
If you already have a gauge connected
You will not need a pullup resistor - the gauge's internal circuitry already provides one. You will only need to tap into the existing signal feeding the fuel gauge sender. Jump to the calibration process below.
  • Note you will need to ensure the sender does not exceed 5v during calibration. if it does, you will need an additional voltage divider to scale the voltage down to 0-5v required by the RaceCapture input.
If you have no gauge / you want to only use RaceCapture for your dashboard gauge
If you only have the sender and want to directly integrate with RaceCapture's analog input, follow this procedure.
  • Choose a pull-up resistor value based on the the sender's ohm range. If it is less than 1000 ohms, then choose a 1000 (1K) ohm resistor as your pull-up. If the sender range is higher than 1000 ohms, choose a 2.2K resistor.
    • Rule of thumb - choose a resistor that is about 2X to 4X the maximum resistance of the sender.
    • A 1/2 watt, 1% accuracy resistor is recommended.
Calibration
  • Empty (0%)
  • 1/4 (25%)
  • 1/2 (50%)
  • 3/4 (75%)
  • Full (100%)
Set up the Analog Channel
  • Choose an available analog input for your Fuel Level channel, then select the basic fuel level preset by selecting FuelLevel in the dropdown list.
    • This pre-sets the units (%), logging precision and min / max values. You can edit this by pressing the gear button next to the channel name.
  • Set the sample rate to 1Hz.
  • Set the mode to Mapped. This will let you create a curved mapping for the sensor voltage.
  • Set the smoothing to Maximum - this will help account for variances due to fuel slosh.
  • Enter the mapped values noted in the calibration process into the Analog Channel mapping editor under RaceCapture setup. This will provide the calibration curve for your fuel tank.
  • Write these settings back to RaceCapture and observe your fuel level readings in units of percentage.
Sensor Breakout Board
Sensor X instructions
